A diagnostic catalog of the causes & cures of of dimming light fixtures or flickering lights & power losses.
How to diagnose the causes of flickering or dimming lights at or in buildings.
This article gives simple diagnostic steps that a homeowner can do to determine the type of electrical system problem that is causing flickering or dimming lights or intermittent loss of electrical power. We list the common causes of these problems and suggest what to do about them.
Watch out: flickering or dimming lights often indicates a dangerous condition. Switch off the bad acting appliance or circuit and ask for help from a licensed electrician.
InspectAPedia tolerates no conflicts of interest. We have no relationship with advertisers, products, or services discussed at this website.
- Daniel Friedman, Publisher/Editor/Author - See WHO ARE WE?
Watch out: flickering or dimming lights at a building may be more than an inconvenience.
While some causes of flickering lights may be normal and harmless, such as flickering in certain types of light bulbs, many others indicate a dangerous condition, risking fire, shock, injury or worse.
The safest approach is to turn off electrical circuits or components that are causing flickering or dimming or acting strangely in any way.
If you cannot safely access your electrical panel to turn off dangerous circuits or components, leave the building and call your local emergency services.
At FLOOD & DISASTER BUILDING DAMAGE REPAIR PROCEDURES we list emergency numbers for various countries from Australia (000) to the U.K. (112). In Canada or the U.S. call 911. In Mexico call 066.
[Click to enlarge any image]
Photo: a fluorescent light fixture may be the only electrical device that is flickering, for any of several reasons we will explain below. Other causes of flickering lights are very dangerous.
In diagnosing the cause of flickering or dimming lights at a building the following diagnostic questions can help narrow down the cause of the trouble.
In the photo above I am showing the original data tag for this Fox Co. fluorescent fixture installed in the bathroom of a Minnesota home built in 1961.
To stop the flickering light in this luminaire fixture I needed to replace the ballast.
Details of repairing dead, humming, dim, or flickering fluorescent lights are
Watch out: for flickering light safety hazards and take the immediate safety measures listed here.
Start by turning off any electrical appliance or circuit that is misbehaving. If you are not trained and familiar with safe electrical practices and repairs, keep your fingers off of the wiring - you could be shocked or killed or could cause a fire. Call for help from a licensed electrician.
Check your local telephone listings for licensed electricians or
Watch out: flickering or dimming lights may, depending on the cause, indicate a dangerous condition. Arcing or overheating at electrical circuits can ultimately lead not only to power loss but to a building fire.
That's why we recommend turning off misbehaving electrical equipment while you wait for the electrician.
Canada's CCOHS has written some of the most easily understood description of who sees flickering lights, what people can see or sense, and what health effects may occur when exposed to flickering light. Excerpts are below:
People can see lights flashing on and off up to about 50 flashes per second (50 Hz) - they are most sensitive to time-varying illumination in the 10-25 Hz range. The actual critical flicker frequency increases as the light intensity increases up to a maximum value, after which it starts to decrease.
When a light is flickering at a frequency greater than 50 or so Hertz, most people can no longer distinguish between the individual flickers.
At this frequency - the critical flicker frequency or flicker fusion threshold - the flashes appear to fuse into a steady, continuous source of light. This happens because the response to the light stimulus lasts longer than the flash itself.
Most people cannot notice the flicker in fluorescent lights that have a flicker rate of 120 cycles per second (or 120 Hz).
The light flicker may be detected by its stroboscopic effect. When objects move or rotate rapidly, they may be lit at or about the same position during each cycle or rotation.
This makes objects look as if they are moving more slowly than their actual speeds - they may even appear stationary if the object is moving at the same rate as the flicker frequency (or a multiple of it).
This fact is the principle behind a strobe light but it is not the desired effect in general lighting. In fact, it could be a safety hazard if someone mistakenly thought that some equipment was stationary or was moving slowly. - CCOHS, "Lighting Ergonomics - Light Flicker", Canadian Centre for Occupational Health and Safety, CCOHS, retrieved 2015/11/09, original source: http://www.ccohs.ca/oshanswers/ergonomics/lighting_flicker.html
Also, from a different source, we see that flickering light can be a source of eye strain and headaches even if it is not related to electrical malfunctions that we listed earlier in this article:
... the use of high frequency electronic ballasts (20,000 Hz or higher) in fluorescent lights resulted in more than a 50% drop in complaints of eye strain and headaches.
There tended to be fewer complaints of headaches among workers on higher floors compared to those closer to ground level; that is, workers exposed to more natural light experienced fewer health effects. - Wilkins, A. J., I. Nimmo-Smith, A. I. Slater, and L. Bedocs. "Fluorescent lighting, headaches and eyestrain." Lighting Research and Technology 21, no. 1 (1989): 11-18.
This topic has moved to FLICKERING LIGHTS, LOST NEUTRAL
...
Below you will find questions and answers previously posted on this page at its page bottom reader comment box.
I have a 1970s two pin, double fluorescent light in my main bath. The light flickered and died when one tube burned out black at one end. I replaced both tubes and the same tube turned black at one end immediately. So i figured it might be the ballast. When turned on, the light was barely discernable - almost non existent but enough to find my toothbrush.
I've been leaving it for over a year as I will upgrade the lighting when I redo the entire bathroom and a new ballast is almost as expensive here as a newer led light. My question is, after not working for over a year all of a sudden both tubes in the light started to work last night! And again this am.
The one tube with the black end now has black at both ends though. FYI we had some record cold with a wind chill for the last two days. -45 The attic is over the bathroom on the north east corner of the house. There is some ice damning on that corner of the roof as I had new leaf guards installed in the Fall.
I am not going to be turning the light on as I'm quite stumped as to why it would be working all of a sudden after a year. Would like some insight into how this is happening?
When it gets warmer I'll go up in the attic to check the venting and wiring before putting any new parts or a new light in. Thanks much in advance. Puzzled im Canada .
On 2023-02-05 by InspectApedia Publisher - flickering and dying light suddenly worked again
@Dogs_rule,
That sounds as if there could simply be a loose or corroded electrical connection.
On 2023-02-03 by Kate.darling55@gmail.com - lost power after turning on electric heat
I heard a thump and the power went out briefly. None of the fuses turned off. I had just turned out the electric heat to a room I don't usually heat. There was no smell of smoke. I do have mice. How immanently serious is this problem?
On 2023-02-03 by InspectApedia Publisher - heard a thump and the power went out briefly
@Kate darling55,
If you have power everywhere in your home it's possible that the "THUMP" that you heard was outside at a power company's line transformer. ON occasion a power company transformer or its fuse blows, power blinks off, and (luckily for us) there is enough redundancy in the system that power returns to your home via an alternative route.
On 2023-01-03 by Karin Bridges - washing machine causes house lights to flicker
I built a house in 2020. The electrical is having issues. The builder's electrician is stumped, as is the one I hired independently.
The washer is on a separate breaker, yet when it is in its agitation cycle, the lights in the house flicker with the beat. Also, it takes twice as long to cook things like casseroles that I have made or bought from places that come with standard cooking times.
We have had the entire control panel in the oven replaced, and the element is fine. I have also had the connections in the box checked.
Please tell me what else it could be. The electrical panel is an Eaton 200 Amp, and the house is less than 1800 sf. I am at my wit's end trying to solve this and am not sure if the house is safe.
On 2023-01-03 by InspectApedia Publisher - the lights in the house flicker with the beat of the washer agitation cycle
@Karin Bridges,
I appreciate the interesting question but have to duck slightly with the apology that I doubt that we, peering at your home's electrical system through the eye of a needle formed by a brief text, can but guess - your onsite people have to be smarter than we are.
If you're certain that the flickering ONLY occurs when the washer is running, that suggests either a problem with that appliance and / or its circuit, or an electrical problem stimulated by vibration caused by the washer's agitation. Those are clues worth proceeding.
So investigate closely the circuit and connections, starting at the electrical panel. (Something as simple as a corroded or overheated connection or even an aluminum service entry cable that isn't actually very tightly-pinned under the connector-lug-screw can cause flickering lights and other anomalous behaviour in the electrical system).
A connector might look tight and work find when it's not being jiggled around. A closer look is in order.
How electrical connections are made and what devices are used are also critical. Insufficient tightening, back-wiring, using push-in connectors instead of screws, etc. all can cause trouble.
About your oven's cook time, it should be simple to measure the oven temperature and compare it with the setting on the controls. If the actual temperature is close to the control-set-temperature, then the long cook time isn't likely to be related to the electrical system itself. Keep in mind that measured oven temperature is never highly accurate, so just getting in the ballpark of the dial setting is probably all one can expect.
For example "In a nutshell, it’s impossible to control your oven temperature, so you should stop worrying about it altogether—or so writes Slate writer Brian Palmer. While you think might 350 degrees on the dial means 350 in the oven, no residential oven maintains a 350-degree temperature for the duration of a bake session.Rather, it usually ranges between 330 and 370 degrees and, as Palmer notes, that’s if it’s a well-calibrated oven, which few are. What about oven thermometers, you ask? “A waste of time,” writes Palmer.
The variability in temperature throughout the oven chamber makes oven thermometers unreliable at best." - https://www.thekitchn.com/why-you-should-stop-worrying-about-your-oven-temperature-175602
So instead, compare cooking properties of your oven with other owners of the same model and with others of different models and features.
Why would half my power go out when i shut the breaker to my water heater off
On 2022-12-16 by InspectApedia (Editor) - Why would half my power go out when i shut the breaker to my water heater off ?
Watch out: when power is lost in one side of a 220V electrical panel, because of how they are wired, a 220V electric water heater might return current from the live panel side back to the "dead" side of an electrical panel, sending current through the electric water heater's heating element.
As it will be a useful diagnostic for readers on this page, we are re-posting the following discussion with readers Kenneth and Juliet that appeared originally at
https://inspectapedia.com/Manufactured_Homes/Mobile-Home-Electrical-System-FAQs.phpWatch out: I suspect the panel is damaged or mis-wired.
Power to breakers on one side of the panel is perhaps being fed through the water heater breaker instead of from the incoming power source on that side.
A bad crossover connector could also be involved but I don't think that alone would explain the situation that you describe.
Any of those is unsafe.
You should get help from a licensed electrician right away.
Let me know
- what the electrician finds
- the brand and age of the electrical panel
- if there is any aluminum wiring
- the building age & location
Please also post a photo of the panel showing the breakers2022/12/13 Juliet said:
@Kenneth, if you have lost voltage on one incoming line of the 220v in the panel, when the water heater breaker is on it can cause voltage to travel from the one leg of 220v in the panel that has voltage on it thru the water heater element & back to the panel thru the water heater breaker, back feeding 110v to the other leg of the panel buss bar thus putting 110v on the other circuits.
Turn the water heater breaker off & then check to see if you have 220v across the two incoming lines & main breaker.
I think you've lost one leg of the 220v on a main breaker or the incoming line from the meter box.
InspectApedia (Editor) (mod) · 2022/12/13 - said:
@Juliet,
Thank you so much for posting that electrical power loss diagnostic suggestion
"220V Electric water heater can back-power electrical current to one side of an electrical panel"
it's not one that I had come across, and it's very helpful.
On 2022-11-13 by Rob - laser printer causes flickering lights on start up and when printing
Hello - I recently purchased a new laser printer and it cause some light fixture flickering on start up and when printing. Laser printers are known to draw a lot of power on start up and during other activities. The circuit in question is 15A and has a few standard outlets and a few lights on it but the circuit breaker is not tripping.
I can't easily move the printer as it is connected via a USB cable. Do you have any suggestions to solve this problem? Thanks, Rob
On 2022-11-13 by InspectApedia (Editor)
@Rob,
Thank you for an interesting question. It might be diagnostic to try plugging the printer in at another electrical receptacle on the same circuit.
If the lights don't flicker when the printer is used plugged in elsewhere it's possible that the problem is a poor connection or damage at the electrical receptacle where it was plugged in before.Watch out: If the printer is shaking as it prints it's possible that its vibration is moving its power cord or a table on which other electrical devices are plugged in - shaking might reveal loose wiring in the electrical receptavle.
On 2022-11-10 by Joseph cross - lost power in half of trailer home
So I have a 1979 mobile home 2 bedrooms 1 bath that has lost power to the front half which is the dining room, kitchen, and living room. I see this is a common occurrence for most part but its also effected the stove and water heater. Stove has power but oven Don t get hot. Also our water heater completely quit Don t work at all.
What could be my problem? I haven't seen any post with both half trailer missing power and major appliances not working. Any help is greatly appreciated.
I have already had an electrician come look and he said I was fine yet 20 mins after he left the lights in dining room and kitchen flickered almost turning off so I turned most breakers off duty to being worried my home may burn down.
Please someone help if you can. Thank you & have a good day
On 2022-11-10 by InspectApedia (Editor) - half trailer missing power and major appliances not working
@Joseph cross,
Often when large areas of a mobile home have lost power and particularly when more than one individual electrical circuit is involved, I suspect that the problem starts right in the electrical panel.
For example (this may not be your case) it's possible for all of the circuits on one side of an electrical panel to lose power if one of the two main entry cables has been damaged or is poorly-connected. That problem occurs more-often when the entering service entry wires are aluminum.
Losing power in half the panel can explain why your electric stove might seem to work but not get hot: burners have only half the power intended.
You need to find another electrician, one who is experienced and who knows to check the entering service wire connections in the panel.
You might mention that the service entry wire in the panel (or in the electric meter) might LOOK OK in the panel but may in fact be arc-burned or poorly connected.
The electrician should inspect, clean, tighten those connections and if that makes no difference, may have to inspect similar connections in the electric meter base.
These diagnostic Q&A may help
MOBILE HOME ELECTRICAL - FLICKERING LIGHTS
Keep us posted: what you find will definitely help other readers.
On 2022-10-21 by Jay - all of the lights flicker when small appliances are on and some go dim or go off
When the heater or hair dryer or microwave is on lights dim or flicker throughout the house ....in some areas they vey dim or go off completely.
On 2022-10-21 by InspectApedia (Editor) - heater or hair dryer or microwave cause lights to dim or flicker throughout the house
@Jay,
That sounds like
- an overloaded circuit
- a poor or loose electrical connection
- aluminum electrical wire, if not properly repaired, a fire hazard
Or, of course, something else we've not named
On 2022-09-25 by Lee - why do some electrical circuits sometimes lose power, breakers not tripped?
I have some circuits in my house that lose power intermittently. No breakers tripped. If I turn a 220V appliance on, everything comes back on. Any thoughts what might be happening?
Thanks,
Lee
On 2022-09-25 by InspectApedia (Editor)
@Lee,
I suspect a bad or unsafe connection at a breaker in the electrical panel - so your electrician might start there.
What is the brand of the electrical panel in your home?
Where is the home - country and city?
How old are the home and the panel?
Is there any aluminum wiring in the home?
I would leave the offending circuits turned OFF at the panel until your electrician has examined the panel and wiring.
Let me know what your electrician finds - that may help other readers.
Other causes of flickering lights are given above on this page: do take a look.
I just went through your page on Flickering Lights & Electrical Power Loss, an excellent doc, very nice.
I have been having an intermittent, very intermittent, blinking lights problem for a long time, a couple years as memory serves. Diagnosing it is difficult because it is so intermittent. I have tried to find a pattern, anything I can track down and troubleshoot - no luck.
As background, I am an electrical engineer with 40 years of troubleshooting experience in broadcast radio and tv stations including control room design and construction right down to the very last wire. Even mobile trucks. All that to say, I have a lot of diagnostic and troubleshooting experience.
I am pretty sure, though none of us in the house are really certain, it mostly happens in the kitchen. And most evident in the 5-lamp chandelier in the kitchen/dining area. It may be happening in other rooms though it is far less common there. Then again, we spend so much less time in those rooms so maybe we're missing it.
Anyways, and to the point of my question, I would like to be able to monitor the voltage in a few places as a diagnostic step. Are you aware of a monitoring device that I could connect to various outlets (and use an adapter to clip onto lines where there are no outlets) and whose data I could easily see or even download?
My goal is to determine if these dimming glitches are local to one
I'd be grateful for the assistance.
Jay
On 2022-08-08 by InspectApedia-911 (mod) - voltage monitoring device
@jstevans,
Short answer: no, not that I've seen for casual purchase, installation and use.
Yes, there are industrial process systems and devices that can monitor multiple data points.
Our mentor/associate Dr. Jess Aronstein has demonstrated methods of monitoring multiple points on an electrical circuit, though in that case it was for investigating overheating at connections.
It was a labor-intensive and sensor-intensive approach that involved an electrical engineering's expert selection of sensors, installing them, and connecting them to a computer that in turn had supporting software.
There are of course current monitoring and measuring devices on the market, even simple DMMs and VOMs, but not intended for monitoring multiple points.
** What do you think of starting at the electrical panel: monitor individual circuits starting with the one you suspect.
** Take a look at Eaton's "Power Xpert Multi-Point Meter" and let me know if you think that might be useful.
** What do you think also, about the probability that as little as a single mis-behaving device can create a load that shows up back in the panel to cause flickering lights on one or more circuits?
On 2022-08-09 by Jay
@InspectApedia-911, I have considered the "single mis-behaving device" possibility.
I was hoping I could monitor the voltage in enough places to a) confirm that the voltage is actually dropping and b) perhaps localize it physically or to a specific circuit.
I am pretty sure the effect is primarily in the kitchen. The lighting fixture over the kitchen table is where we see this the most often and the most dramatically. This fixture has 5 dimmable LEDs and is controlled by an LED compatible dimmer. This is actually the second LED compatible dimmer, I was suspicious of the first one. One time the effect was so severe the LEDs in the fixture were strobing. OK for a disco, very wrong for our kitchen.
My next step is to replace the LEDs with incandescents or halogens in an effort to determine if the LEDs/dimmer combination is the cause.
Thanks for your assistance. I'll keep digging through and will try to remember to report back.
Thank you again,
Jay
On 2022-08-09 by InspectApedia-911 (mod)
@jay,
You may have already tried this but a simple diagnostic that is usually where I started to turn off individual devices or lights or circuits one by one to see if that lets us quickly hone it on the cause of the odd electrical behavior.
I'm surprised that voltage drop might be the problem here I and suspect as more likely a bad connection or a failing individual electrical device on the circuit.
It's really easy to monitor the voltage level with a DMM or VOM.
We do see much greater service voltage variation in some locations, such as Central mexico, then others such as Canada or much of the US.
On 2022-08-11 by Jay
@InspectApedia-911, Those are excellent suggestions if the problem occurs often enough. Mine is an "every few days for a few seconds that may repeat momentarily or not for days" situation. That's the devil's own problem to troubleshoot. Thus my hope for long-term monitoring.
BTW, I agree it might be a loose connection and once thought I'd found it so I tightened everything - twice to be sure. Nope, came back a few days later.
Thanks again,
Jay
On 2022-08-11 by InspectApedia-911 (mod)
@Jay
And no fluorescents, no ballasts, no timers, etc, right?
Does the flicker occur when there is a load surge such as a refrigerator or freezer or A/C unit turning on?
On 2022-08-13 by Jay
@InspectApedia-911, I opened the box with the dimmer in it and checked every single connection, I wiggled and pushed and twisted - not a single blink.
Then I saw a little switch or adjustment level on the dimmer I didn't remember having seen when I installed it. So, off to the Internet to find the installation guide. It was a little tiny adjustment lever to set the low-brightness adjustment.
But while I was looking at the installation instructions I saw mention of a "list of compatible LEDs for this dimmer." Back to the Internet where I found the list, which had a handy search tool into which I entered the model of the lamps I have had installed for a couple years - the dimmer manufacturer rates them as only 3 stars out of 4 on the blinking scale.
Whoa, I'd never heard of needing to match LEDs to the dimmer. I did some more research, found a 4-star non-blinker and am awaiting delivery. Maybe, maybe it has always been a mismatch.
TBD.
Jay
On 2022-08-13 by InspectApedia-911 (mod) - list of compatible LEDs for this dimmer
@Jay,
Thanks so much for that update that's interesting and helpful.
I didn't think to suggest that to you but in fact I have, earlier in the life of LEDs, run into cases in which some of the early models were not dimmable.
(As was the case, of course, with fluorescent lights.)
Certainly the least expensive would be to try and existing incandescent bulb in those fixtures to see what happens with your dimmer switch.
Halogens are a bit more efficient but I would prefer to end with a dimmable LED both for Energy savings and in another sense simply because the bulbs run cooler which tends to make less trouble for the fixture in which the bulb is mounted.
A clue is that you will see some LED products mentioned on the packaging that they went can work with dimmers. That's an indirect warning that there are some others that don't work with dimmers and of course there's some variation and how the dimmer switches work themselves.
On 2022-07-06 by Texas Homeowner - flickering lights, aluminum wire, possible improper and unsafe "repair"
Hi all, thanks for the informative website.
I have pigtailed two circuits in my 70s-era home with Alumiconn connectors, however both of the circuits have an issue with light flicker when using another device on the circuit. For example, the floor lamp exhibits a solid on/off when turning on a fan on the same circuit.
This issue presents itself on the closest outlet to the breaker. Any idea on troubleshooting? I had an electrician look and he said it could either be a loose neutral connection, possibly in a j-box between the outlet receptacle and breaker.
I'm a bit concerned that this problem is caused by the Alumiconn installation as only these two circuits are showing this issue. I used the proper stripping length and torque screwdriver.
On 2022-07-07 by InspectApedia-911 (mod)
@Texas Homeowner,
Watch out: I'm concerned as well about the possibility of an electrical fire. I don't know whether the problem is in the connectors that you installed or whether the problem is that you've done an incomplete repair on aluminum wiring circuit. Every single connector in the whole installation needs to be addressed.
You will see it on the page above a very thorough list of causes of flickering lights on circuits. And while you might want to look through that I think we first need to address the question of whether you're aluminum wiring has been properly repaired.
I commend you for using a torque measuring screwdriver I thought I was the only person who owned one. Most electricians have never even seen one much less carried one in their toolbox. But still I don't think that that connector was intended to be used by a homeowner.
The first place to start is to examine the connectors that have been installed because of the possibility that a space limitation or jamming them back into electrical box may have actually caused a connection to be less tight than you thought.
Second just to review your entire electrical wiring system to make sure that the repair is complete and correct by ( as I am obligated to say ) a trained installer.
On 2022-06-25 by Carrie white - hair straightener trips circuit breaker
I was vacuuming n my daughter was in the bathroom straightening her hair the breaker kept flipping off.i turned everything off fans n air-conditioners eventually all the power stayed off in our bathroom and bedroom n part of our laundry room
changed the outlet in the bathroom since it's the ones with the buttons and seems to control other power in other rooms didn't help tested the breaker by switching to another part of the house (dishwasher) it still powered it on any idea what it could be
On 2022-06-04 by Thom - fluorescent bulbs won't light reliably
Looked through your resources. Very helpful and explanatory. My pair of fluorescent bulbs won't light reliably when powered on (maybe 10% of the time) unless I take off the cover and tap on one specific spot on only one of the bulbs – nowhere else. That will make it turn on nearly every time and both bulbs will ignite.
If I turn off the power and then it back on, the bulbs will not turn on unless I tap that one spot on one bulb again.
Inconvenient to say the least when it's the only light source in our laundry room...
Help?
On 2022-06-04 by InspectApedia-911 (mod) - pair of fluorescent bulbs won't light reliably when powered on
@Thom,
Yep. We had that problem with lights over a kitchen counter in a 1960s home in Two Harbors MN.
FLUORESCENT LIGHT REPAIRS has a lot of detail on this
You may need to
- find a loose connection anywhere in the circuit, but often at the lamp connectors
- replace bad bulbs
- replace a bad transformer
- replace one or more bad bulb contact-mounts
Finally my champion brother-in-law took the task of doing just that and the lights have since worked perfectly.
On 2022-06-01 by matt - where to look for loose electrical connections in mobile home - Fleetwood doublewide
hello i have a 2001 fleetwood double wide that i have lost power to the back 1/4 of my home i checked all the breakers & changed the recepticales on the back half of my house i'm thinking it's a junction box but not sure where to look .
On 2022-06-01 by InspectApedia-911 (mod) - causes of flickering lights in manufactured homes
@matt,
Provided that you've first checked out the obvious and dangerous causes of flickering lights given above on this page,
and we're really talking about an actual loss of electrical power,
then
You could have a bad crossover connector between home sections.
See MANUFACTURED HOME CROSSOVER CONNECTORS https://inspectapedia.com/Manufactured_Homes/Mobile-Home-Electrical-Crossover-Connectors.php
On 2022-04-13 by Robert - water heater makes lights flicker
My lights flicker when my 80amp tankless water heater is running. It is hooked up to my main 200amp service box and the lights are on connected to my inside 100amp box inside.
On 2022-04-13 by Inspectapedia Com Moderator - what else the electrician may check on flickering lights
@Robert,
Your electrician may find some things to check besides the rather lengthy list of causes of flickering lights that we give above on this page, but I hope you will review that list, as it's more complete than I can make up de novo here.
Remember to check carefully the connections on any aluminum wire circuit connections such as may be powering an electric water heater.
On 2022-01-18 by Mahmoud Salem - lights flicker on top floor in building
Hi,
The lighting in the top floor flickers and the circuit breaker turns to off. No signs of burns or cut wires. Is the circuit breaker faulty? Took it to shop and was checked and I was told it was ok!
Thanks
On 2022-01-18 by Inspectapedia Com Moderator
@Mahmoud Salem,
It could be a bad circuit breaker but more likely is a loose electrical connection, or one of the other causes listed in the article above. Please look through that information and keep me posted.Also look for roof leaks that wet an electrical box or connector.
On 2021-11-30 by Robert Gillitzer - overheating electrical connections can cause flickering lights
I have one circuit that has several outlets & 3 lights on it. When I switch on any of the lights, or plug into one of the outlets, that one or all, depending if I have more than one light one, all will flicker.The light switches have been replaced, but the lights still flicker.
Is it possible for one of the switches or outlets to affect any or all the connections on that line? Or should I be looking at the main box for a loose connection of that line. All the other lines in the house are ok
On 2021-12-01 by Inspectapedia Com Moderator - loose or overheating electrical connections can cause flickering lights
@Robert Gillitzer,
For sure a loose or overheating connection anywhere on the circuit, from the electrical panel to the light fixtures and receptacles involved could cause flickering lights.
By the way, usually we don't put both receptacles and fixed lighting on the same circuit.
On 2021-11-28 by Warren - sub panel causes flickering lights
i have a separate part of the house that has a sub panel with 4 breakers and from time to time different lights within those 4 circuits goes out randomly and then randomly come back on without tripping any breakers what could be causing this type of problem ?
On 2021-11-28 by Inspectapedia Com Moderator - causes of flickering lights are listed here
@Warren,
Most likely the cause of your flickering lights is one of those described above on this page.
Watch out: there are some brands of electrical panel (e.g. FPE Stab-Lok, Zinsco, and others) and some electrical wiring (solid aluminum branch conductors) for which flickering lights are a big red flag of imminent danger of a building fire.
On 2021-10-29 by James D - TV remote causes flickering lights?
I have a small LED night-light that is plugged into a wall socket in my bedroom.
My question is when I use the TV remote (Fire TV) it makes the night light flicker. Also, when we turn off or on the ceiling fan/light switch, a small table side lamp (that can turn on and off when you touch the base) will turn on if the table lamp is off, and off if the table lamp is on.
I am worried about how our home was wired since the contractor was "El Cheap-o" on materials and labor. Any thoughts or suggestions?
On 2021-10-29 by inspectapedia.com.moderator - problem electrical circuits need more diagnosis
@James D,
That sounds like a wiring error or possibly, if we're lucky, simply a loose electrical connection somewhere on that circuit.
But
Watch out: such connections can be dangerous, causing arcing and overheating.
- How old is the home?
- When was the wiring job done?
- Was the installer a trained, licensed electrician?
- Were aluminum wire or aluminum components used ? (A particular fire hazard for branch circuits)
Best would be to get an experienced, licensed electrician to trace and diagnose the problem circuit.
Depending on what she finds, that in turn may be suggestive of inexpert workmanship; if so then further inspection of the home's wiring and electrical panel and devices would certainly be justified.
On 2021-08-23 by dave - dimmer switch makes lights flicker on and off
we turn om lights to the house and lights flicker after a period of time when dimmer switch is on why?
On 2021-08-23 by inspectapedia.com.moderator - look for a loose electrical connection or overheating at a light dimmer switch
@dave,
Of course there could be another problem but the common explanation for the flickering lights that you described would be a loose electrical connection at the switch or an overheating switch. I would have the switch replaced.
On 2021-07-24 by Sully - all lights blink briefly when some appliances run
The lights on all 15a circuits in entire home blink momentarily when HVAC compressor or vacuum cleaner plugged into 15a outlet starts? 20a circuits don't seem to be issue. Blink happens for both L1 & L2 circuits.
On 2021-07-24 by mak.church (mod) - too much current draw for a 15A but not 20A circuit can cause flickering Lights?
@Sully,
In the above article, there are a number of diagnostic steps that are worth looking at. Because of your reference to both 15A and 20A circuits however, pay specific attention to the section:
18 Causes of Dimming or Flickering Lights or Electrical Power Loss at Buildings
and the #2 item there: Appliance or motor drawing high current
Perhaps the high current draw in this case is just enough to blink or dim lights on a 15A but not on a 20A circuit.A guess is that the two devices you cite are drawing a moment of high current at start-up (not un-common). On a 20A circuit the current drawn is tolerated because the circuit permits a bit more current than the 15A wires;
A corroded or loose connection in a circuit or in a panel might cause that trouble too, but as you're seeing it on both sides of the panel I suspect our first guess is the right one.
Let us know if you have additional questions.
On 2021-06-25 by John - worried about electrical wiring in a 1970's home
Hello, i bought a house that had its electrical wiring updated in the 70s. When they did it, they did not dedicate a circuit for each room so some rooms share circuits.
In my small office I had my computer with monitor and when someone turns on the bathroom ceiling light my computer monitor power turns off - it does this consistently.
I am worried because the computer monitor is LED, uses low power and the light bulb in the bathroom also is LED.
I do not have any high intensity applicances on in my room, just laptop, LED monitor and sometimes a fan and light.
Does this indicate bad or wiring that should be replaced? My concern is that the previous owners were very frugal and likely has the wiring done by unlicensed electricians.
On 2021-06-25 by mak.church (mod) - copper wiring doesn't need replacement based on age alone but watch out for aluminum wire
@John,
Except where your electrical wiring was improperly sized in the first place or where it has been damaged by a building event such as a fire, it is quite rare that it is ever necessary or even appropriate to replace the wiring itself. Copper doesn't wear out. Copper thousands of years old has been found intact in the Egyptian tombs.
It could be a problem with connectors, or an overloaded circuit. Simply turning on the bathroom light should be such a trivial load on the circuit but I suspect there is an unsafe connection or switch for which you need an electrician who will locate and fix the connector, switch, or device.
Because it's expensive to bring an electrician to a property for a single small problem, that would be a great time to have the electrician add a dedicated electrical circuit to the room where you use your computer.
Watch out: 1970s electrical wiring could include aluminum solid conductor branch circuit wires. If your home has aluminum wiring and the wiring has not been properly repaired by installing the special connector at each and every connection then that circuit is unsafe and is a fire hazard.
So be sure to have your electrician check promptly for the presence of aluminum wiring. Let us know what you're told.
On 2021-06-26 by John - how do I identify aluminum wiring
@mak.church, Thank you. I think the work done in the 1970s was to increase the amps in the home. I confirmed it was not done by a electrician - instead it was done by a family member who is very handy with homes. (Make me nervous). The home was built in the late 1940s and is a two family. It now has 100 amps per apartment.
Is there anything I can do that would help you identify whether I have aluminum wiring such as taking a photo? I will have an electrician come to check regardless but appreciate an unbiased opinion
On 2021-06-26 by inspectapedia.com.moderator (mod) - check flickering light circuit for aluminum wiring
@John,
Your electrician will be able to tell immediately if there is aluminum wiring in the electrical panel when she opens the panel cover to inspect the circuits inside.
That's not something you should do as you could be shocked or killed.
However if you look at any electrical wiring that is visually accessible you may occasionally see printed on the plastic covering of plastic wire the word "aluminum" which would be significant.
You can also use the on-page search box to search this website for
ALUMINUM WIRING HAZARDS & REPAIRS - overheating or corroded connections can cause flickering lights
For an article describing other wiring text or imprint or size that identifies it as an aluminum product.
From the age of your house, the original wiring would not be aluminum.
On 2021-06-26 by John - electrical outlets have reversed polarity
@inspectapedia.com.moderator, thank you. I will definitely not be attempting to investigate or fix beyond what you suggested. I have a great deal of respect for this things and experienced electrical shock as a child!
I just recalled that when we bought the home we did have an electrician over as part of renovating two rooms. He replaced some switches and install a number of new outlets. He did find two switches quite old that needed replacing. My hope is that he would have noticed the aluminum but I’ll have someone check regardless.
However I believe he did not investigate or check the other rooms in the home as I just checked a number of outlets in these rooms and they have reverse polarization which I know is not usually a big deal but thought to ask if it could have any relation to the issue with my computer.
The outlet the computer and monitor are plugged into has reverse polarization.
On 2021-06-26 by inspectapedia.com.moderator - investigating causes of flickering lights - don't forget to check for aluminum wiring
@John,
Thanks for the added detail; keep us posted;
Certainly some of my warnings will err on the side of safety.See USING an ELECTRICAL RECEPTACLE TESTER to CHECK VOLTAGE & WIRING
Watch out: an electrical receptacle with reversed polarity can be unsafe and in some cases can damage electrical equipment. It may not be obvious, after all it's "alternating current" running in "two directions" on the circuit, between hot and neutral.
But keeping the neutral side "live" as what happens in reversed-polarity circuits can actually damage some printed circuits and control boards by delivering power where it is not expected to be fed.
On 2021-06-16 by Cori - expensive bill for fixing flickering lights
I have flickering and dimming lights thought out the whole house. Electrician is here now.
He is replacing my outside main wire and will replace 3 or 4 breakers on panel but says it' NOT GUARANTEED the flickering and dimming lights will stop. R u kidding me?? I'm paying him $1850.00!
On 2021-06-16 by inspectapedia.com.moderator (mod)
@Cori,
Before the electrician leaves ask him to observe whether there are any flickering lights and ask him if there's something else that he recommends
On 2021-05-24 by Zach - Whenever I turn my kitchen light on my dining room fan/light combo dims.
Whenever I turn my kitchen light on my dining room fan/light combo dims. It stays dim until I turn kitchen light off. At first I thought it was possibly in the switch as it's a double switch with power hooked to the top that controls both the top and bottom switch. There is also a 3way switch in the same location ran on a separate breaker.
I turned off both breakers took both the dining room light and kitchen light off the switch and hooked each one directly to the power feed with wire nuts. One connected to one circuit and the other connected to the circuit that the 3way had been on. I flipped on one breaker and dining light came on. I flipped on the other breaker and kitchen light came on.
Again dining room light dimmed as before. I've checked and tightened all wiring going to both fixtures. Help!
On 2021-05-24 - by (mod) - Whenever I turn my kitchen light on my dining room fan/light combo dims
@Zach,
That sounds like a shorted electrical circuit, switch, or fixture.
Your electrician will probably use a DMM or VOM to check for shorting and check the current draw on each of those circuits and also she'd inspect the electrical panel itself, the breakers and the bus - for arcing.
Is there aluminum circuit wire in the building?
What's the electrical circuit brand?
How old is the building?
On 2021-03-21 by Vernon - had a circuit that controlled 3 outside motion lights fail.
Recently I had a circuit that controlled 3 outside motion lights fail.
I checked for proper voltage at the switch and got "0" voltage reading.
Then I checked for voltage at the circuit breaker and it measure 117v.
Then two days later I'm assuming the same or neighboring circuit failed which controls 5 outlets which have a washer, small firdge, garage door opener, and some small devices.(6outlets) I noticed that all of these circuits arent even isolated to certain areas of the house , they seemed to be mixed up.
this house was built in the 60's with what appears to me as some renovation along the way with poorly added circutry.
3 years prior to all these issues dimming of lights when washer and or dryer is in use, as well as bzzing in swiches was present.
Any comments as to what the next step or solution to this problem would be is greatly apreaciated.
On 2021-03-21 by (mod) - outside motion light circuit failure
If that were my home I'd have a licensed electrician trace the circuits involved, both to find the arcing or loose connectors, other unsafe connections and devices, and/or to get clear on what's wired on what circuit: we may need to add circuits to correct an overloading problem as well as fixing the wiring problems.
On 2021-03-24 by (mod) - Unsafe wiring, flickering lights, lost neutral, bootleg ground, moisture damage in a tropical environment home
This diagnostic discussion has moved to its own page
at FALSE GROUND, BOOTLEG & FLICKERING LIGHTS
...
Continue reading at FLICKERING LIGHTS, LOST NEUTRAL, or select a topic from the closely-related articles below, or see the complete ARTICLE INDEX.
Or see FLICKERING LIGHT DIAGNOSTIC FAQs - questions and answers posted originally at this article
Or see these
ELECTRIC POWER LOSS / FLICKERING LIGHTS at InspectApedia.com - online encyclopedia of building & environmental inspection, testing, diagnosis, repair, & problem prevention advice.
Or see this
Or use the SEARCH BOX found below to Ask a Question or Search InspectApedia
Try the search box just below, or if you prefer, post a question or comment in the Comments box below and we will respond promptly.
Search the InspectApedia website
Note: appearance of your Comment below may be delayed: if your comment contains an image, photograph, web link, or text that looks to the software as if it might be a web link, your posting will appear after it has been approved by a moderator. Apologies for the delay.
Only one image can be added per comment but you can post as many comments, and therefore images, as you like.
You will not receive a notification when a response to your question has been posted.
Please bookmark this page to make it easy for you to check back for our response.
Our Comment Box is provided by Countable Web Productions countable.ca
In addition to any citations in the article above, a full list is available on request.